Danesmoor Greenstar 12/18 Oil burning Condensing boiler.
No HW this morning.
Boiler locked out, but upon reset fan ran, purge completed ok, ignition ok .... then cut out.
Replaced manky nozzle, did full service, checked oil present.
No joy.
Had to be solenoid or flame detector.
Remove photocell connector from control box.
Same symptoms.
Reset, then as soon as ignition had occurred, shorted photocell contacts in control unit.
All fine.
Double-checked and proved.
New part 16 sovs.
Job's a good 'un.
(Can't actually run it with the contacts shorted as the sequencer doesn't like it: Leccy shower in play and kettle on standby until Postie arrives)