I've got an intermittent fault (again), on the house boiler.

Could be the pump or the circuit board (I think it's the board myself)

Have a gander at the following flow chart, there seems to be no point where the pump can be diagnosed as the problem.

Boiler Circuitry.JPG
 

Lazarus

Retired Moderator
Joined
May 29, 2009
Messages
27,082
Reaction score
8,669
Points
113
My Satellite Setup
80cm Motorised.
Several small Dishes.
Much else.
My Location
North York Moors
Well you can further eliminate (or otherwise) the Pump by removing it, dismantling the impeller housing and manually freeing it off: Most apparent Pump failures are actually stalling caused by foreign bodies (swarf) and can be easily remedied. They rarely burn out.

The down side is that stalling is generally continuous rather than intermittent so I'm inclined to agree the cause lies elsewhere.
 

MarkW

Regular Member
Joined
Jan 28, 2014
Messages
108
Reaction score
63
Points
28
Age
64
My Satellite Setup
1.2 Galaxy,IBU single,Technomate 5402M3
My Location
Jesi,Italy
Common cause of intermittent problems like this is a dry joint on the circuit board.Have a look at the soldering of the circuit board connector for the pump.You may have to use a magnifying glass,also check the pins and connector.If there are fine cracks it will need re-soldering. What exactly goes wrong?Normally when a pump stops there's an almighty noise when the boiler overheats.
 

Vipersan

Emmett Browns Ghost
Joined
Jun 29, 2009
Messages
10,918
Reaction score
6,663
Points
113
Age
66
My Satellite Setup
IP9000HD +
TD110 Dish and TD88 Dish in Tandem
66°East to 60°West.
AZbox PrmHD + OpnbxS9HD + Skybox + DrHD F15
2x VboxII AZ-EL
2 m+ Alcoa PF + BSC421 C-Band lnbf...
+SS2/TwHnS2-3200 pci/TBS6925 pci
1.5 Fortec Star -Gbox - HtoH Ku/Ka/C
My Location
UK
If there are relays on the control board ..they are always suspect..
not o/c coils ...just arcing on the contacts causing pitting and occasional intermittancy.
A temporary fix can be had by opening the the relays (if faulty) and a light cleaning with emery paper.
But if confirmed faulty ..they really need replacement ..
min 240v 10amp if memory serves.
rgds
VS
 

Channel Hopper

Suffering fools, so you don't have to.
Staff member
Joined
Jan 1, 2000
Messages
35,594
Reaction score
8,575
Points
113
Age
59
Website
www.sat-elite.uk
My Satellite Setup
A little less analogue, and a lot more crap.
My Location
UK
Well you can further eliminate (or otherwise) the Pump by removing it, dismantling the impeller housing and manually freeing it off: Most apparent Pump failures are actually stalling caused by foreign bodies (swarf) and can be easily remedied. They rarely burn out.

The down side is that stalling is generally continuous rather than intermittent so I'm inclined to agree the cause lies elsewhere.

The system used to start straight away after the heating was put on, and a varying number of minutes after a demand for hot water. Nowadays though ity could be up to an hour before the boiler kicks in.
When it does start though the pump makes no out of the ordinary noises, and runs fine until the system is shut off. The flow chart shows a check for 240v across X3 (pump connections ?), and when there is no start, there is no voltage.

Will take the board out for a closer inspection tonight, though I ought to find where I left the solder first.
 

MarkW

Regular Member
Joined
Jan 28, 2014
Messages
108
Reaction score
63
Points
28
Age
64
My Satellite Setup
1.2 Galaxy,IBU single,Technomate 5402M3
My Location
Jesi,Italy
So I assume the gas doesn't light either?I assume this is a combination boiler where all is included ie pump and there's no hot water tank?Normally on a combi before the gas is lit, and the pump started, the fan is started to expel exhaust fumes.To make sure this has happened there's a vacuum switch connected to near the fan,by a tube, so when the fan is on there's a vacuum and the switch goes short circuit,allowing the boiler to start.Check in this area,is the fan starting,is the switch going short circuit(voltage across goes to zero).Good luck
 

Vipersan

Emmett Browns Ghost
Joined
Jun 29, 2009
Messages
10,918
Reaction score
6,663
Points
113
Age
66
My Satellite Setup
IP9000HD +
TD110 Dish and TD88 Dish in Tandem
66°East to 60°West.
AZbox PrmHD + OpnbxS9HD + Skybox + DrHD F15
2x VboxII AZ-EL
2 m+ Alcoa PF + BSC421 C-Band lnbf...
+SS2/TwHnS2-3200 pci/TBS6925 pci
1.5 Fortec Star -Gbox - HtoH Ku/Ka/C
My Location
UK
Just read Marks reply ..and it made me remember something..

...on mine there is also a fan near the flue (top of combustion chamber) which activates a switch via plastic tubes ..ie pressure driven.
This does go faulty ..but also blocks up..
I had this happen once and was advised on a plumbing thread to change the unit..
On my boiler referred to as the 'Venturi device'..
Well I dug a little deeper ..and found that this device rarely fails ...but simply blocks and is easily fixed....by disconnecting the 2 rubber tubes attached to it ..and blowing a good lungful of air as hard as possible through the unit ....pipe in mouth ...then reversing the procedure and blowing air in the opposite dirction through the other pipe..
Result ..after reconnecting the tubes the boiler kicked up and remained working ..
I did this over 4 years ago ..and have had other boiler issues since ..but NOT with the venturi.
Mebbe you have something similar on yours ?

The point being ..If the venturi/fan assembly cannot expel flue output...
The boiler refuses to start and /or can shut down.
Protection from fumes build up..
rgds
VS
 
Last edited:

Channel Hopper

Suffering fools, so you don't have to.
Staff member
Joined
Jan 1, 2000
Messages
35,594
Reaction score
8,575
Points
113
Age
59
Website
www.sat-elite.uk
My Satellite Setup
A little less analogue, and a lot more crap.
My Location
UK
Thanks, but the air pressure switch (and fan) are further down on the flow chart, which suggests these do not have a direct impact on the start up.

The flow chart could be at fault though, hence my original question
 

Vipersan

Emmett Browns Ghost
Joined
Jun 29, 2009
Messages
10,918
Reaction score
6,663
Points
113
Age
66
My Satellite Setup
IP9000HD +
TD110 Dish and TD88 Dish in Tandem
66°East to 60°West.
AZbox PrmHD + OpnbxS9HD + Skybox + DrHD F15
2x VboxII AZ-EL
2 m+ Alcoa PF + BSC421 C-Band lnbf...
+SS2/TwHnS2-3200 pci/TBS6925 pci
1.5 Fortec Star -Gbox - HtoH Ku/Ka/C
My Location
UK
Thanks, but the air pressure switch (and fan) are further down on the flow chart, which suggests these do not have a direct impact on the start up.

The flow chart could be at fault though, hence my original question
Back to suspecting the control pcb I think..
 

MarkW

Regular Member
Joined
Jan 28, 2014
Messages
108
Reaction score
63
Points
28
Age
64
My Satellite Setup
1.2 Galaxy,IBU single,Technomate 5402M3
My Location
Jesi,Italy
Fair enough but is the fan coming on when the fault on?
 

2cvbloke

Regular Member
Joined
Jan 5, 2006
Messages
9,768
Reaction score
1,808
Points
113
Age
38
My Satellite Setup
No satellite stuff for the moment (aside from a 43cm minidish that was on the house already), Samsung SyncMaster T27B550 Smart TV & Monitor, and a few computers...
My Location
Near Pontop Pike, Co. Durham
google the make & model (I would have, but, there's none posted), probably someone out there with the same fault and a solution, or just call an engineer in, just incase it's serious... :)
 

Vipersan

Emmett Browns Ghost
Joined
Jun 29, 2009
Messages
10,918
Reaction score
6,663
Points
113
Age
66
My Satellite Setup
IP9000HD +
TD110 Dish and TD88 Dish in Tandem
66°East to 60°West.
AZbox PrmHD + OpnbxS9HD + Skybox + DrHD F15
2x VboxII AZ-EL
2 m+ Alcoa PF + BSC421 C-Band lnbf...
+SS2/TwHnS2-3200 pci/TBS6925 pci
1.5 Fortec Star -Gbox - HtoH Ku/Ka/C
My Location
UK
google the make & model (I would have, but, there's none posted), probably someone out there with the same fault and a solution, or just call an engineer in, just incase it's serious... :)
I have a feeling CH want's to deal with this himself ..
I know I would ..
Not afraid to tackle any boiler problem ..but I draw the line ___sensibly___ when it comes to the gas.
Gas = Time to call a trained professional..
 

Terryl

Specialist Contributor
Joined
Apr 14, 2011
Messages
3,276
Reaction score
1,939
Points
113
Age
82
My Satellite Setup
OpenBox X5 on a 1 meter motorized dish.
And now a 10 foot "C" band dish.

Custom built PC
My Location
Deep in the Boonies in the central Sierra Nevada mountains of California.
My experience with heating boilers not starting or running as long as they should led to some problems with the "Over temp" switch being faulty, most systems (well the newer ones here Stateside do) have an over temp, low water or other safety cutoff switch, if one of these hummers goes bad or intermittent you can loose some hair looking for a fault in the controller board.

Look through the schematic (if you have one) and see if there is an over temp, over pressure or low water sensor/cutoff switch in the circuit somewhere, a simple check with a DVM can tell you if it is out to lunch, (careful as you may have to do this with the system powered down) a bypass clip or jumper can tell you if it is the problem or not, just be careful.

One system I looked at had an over temp switch that had tripped, found out that there was a very small hard to find reset button on it, pressed that and it worked fine, it tripped a few days later, replaced the switch and all was well.

As far as GAS goes, I use about 2 tea spoons of baking soda in a glass of water, works faster then the over the counter stuff.
 

Channel Hopper

Suffering fools, so you don't have to.
Staff member
Joined
Jan 1, 2000
Messages
35,594
Reaction score
8,575
Points
113
Age
59
Website
www.sat-elite.uk
My Satellite Setup
A little less analogue, and a lot more crap.
My Location
UK
Resoldered as many connections as I can see on the board, there are small IC's on the rear of the panel that are impossible to deal with though.

Double checked the thermistors in the demand piping and they check out. The manual states that if there is a 5V between the pins to the DHW switch when there is a damand then it's either the water regulator switch, wiring, or the board. I've checked the first two, though I cannot get to the mechanical regulator itself as it is behind a very awkward 24mm brass nut.
 

Lazarus

Retired Moderator
Joined
May 29, 2009
Messages
27,082
Reaction score
8,669
Points
113
My Satellite Setup
80cm Motorised.
Several small Dishes.
Much else.
My Location
North York Moors
Would I be right in remembering you had a dicky Diverter valve not so long ago - or was that VS?

Not sure if or how that might be relevant, but presumably it reports its state to the Control Board?
 

MarkW

Regular Member
Joined
Jan 28, 2014
Messages
108
Reaction score
63
Points
28
Age
64
My Satellite Setup
1.2 Galaxy,IBU single,Technomate 5402M3
My Location
Jesi,Italy
If you have a 2 or 3 port diverter valve then you don't have a combination boiler.This would be my first port of call(pun intended).They can get sluggish and take time to move and make the circuit that starts the boiler.You can take the actuator off and see how easy it is to manually turn the valve.Make a note how how the actuator comes off and the position of the valve, when you do this.Cheers
 

Channel Hopper

Suffering fools, so you don't have to.
Staff member
Joined
Jan 1, 2000
Messages
35,594
Reaction score
8,575
Points
113
Age
59
Website
www.sat-elite.uk
My Satellite Setup
A little less analogue, and a lot more crap.
My Location
UK
If you have a 2 or 3 port diverter valve then you don't have a combination boiler.This would be my first port of call(pun intended).They can get sluggish and take time to move and make the circuit that starts the boiler.You can take the actuator off and see how easy it is to manually turn the valve.Make a note how how the actuator comes off and the position of the valve, when you do this.Cheers

Diverter valve is not the problem, plunger working as it should when demand is there
 

MarkW

Regular Member
Joined
Jan 28, 2014
Messages
108
Reaction score
63
Points
28
Age
64
My Satellite Setup
1.2 Galaxy,IBU single,Technomate 5402M3
My Location
Jesi,Italy
If you have a hot water tank the thermostat on that can give funny problems.Like all is well until the tank is up to temperature then the boiler stops for the heating.Found that the plastic cover was stressing the control knob and effecting the contacts.Keep going!You're wearing the bastard down.
 

bim

Member
Joined
Jan 2, 2008
Messages
224
Reaction score
202
Points
43
Age
67
Location
lat 45.3301 lon 14.1822
My Satellite Setup
humax foxsat Thomson Tsr200 Pace 3100 Black pro quad dvbs2 80 and 100cm dishes
My Location
croatia Lat 45.3301 Lon 14.1822
If it was a combi boiler (but I think this has been eliminated ) expansion pressure vessel low pressure in this can cause all sorts of problems ie over heating, causing thermal cut out etc. Also this can cause the pump to act irregular. From memory I think it should be 1.5 bar with a bike pump.
 

Channel Hopper

Suffering fools, so you don't have to.
Staff member
Joined
Jan 1, 2000
Messages
35,594
Reaction score
8,575
Points
113
Age
59
Website
www.sat-elite.uk
My Satellite Setup
A little less analogue, and a lot more crap.
My Location
UK
If it was a combi boiler (but I think this has been eliminated ) expansion pressure vessel low pressure in this can cause all sorts of problems ie over heating, causing thermal cut out etc. Also this can cause the pump to act irregular. From memory I think it should be 1.5 bar with a bike pump.


It is a Combi 82 (Wickes/|Halstead) and yes there has been an issue with a loss of pressure before now. I did pump up the expansion chamber a few weeks ago, but will look into trying it again. There has been no thermal cutout for a while.

The boiler did start up normally this morning, so I may have got rid of whatever breaks there were on the board, but I'm still convinced it needs replacing.

There is no hot water tank in the system, nor room thermostat.
 